The compressor used in a water-cooled air conditioning system is short cycling. A service check determines that the suction pressure remains above the normal cut-in point during cycling and that the discharge pressure rapidly builds up to the cut-out point while running and gradually falls to the cut-in point during the off cycle. What is likely the cause?
Official USCG Answer & Rule Citation
Correct Answer: Option B — reduction in condenser water flow (scaled condenser)
Under USCG National Maritime Center examination standards, the accepted correct answer is: reduction in condenser water flow (scaled condenser).